µTasker Forum > MODBUS
Modbus RTU on TWR-K20D72M
Felix:
Hi Mark,
I think I almost have it now! :D
You was right (again ;) ) with the short circuit (it was on the soldering) and I had to change some things in the example.
There´s some communication on all lines now and the slave answers at the given address. Unfortunately there´s still a little problem. How you can see in the attached image the master receives just semi-valid messages. Some bytes are not received correctly, but the Modbus settings on both devices are equal.
Can I fine-tune the timing somehow? Or maybe I'm still doing something wrong?
Best Regards
Felix
mark:
Felix
At 9600 Baud there should be no issues with speed/timing.
If I understand it correctly there are responses (RX) but they don't look to be reliable in some way. I would therefore carefully check the RS485 direction control and signal integrity - at least the response should be identical in each case.
Regards
Mark
Navigation
[0] Message Index
[*] Previous page
Go to full version